Hi
@macca
If your talking about a means of compliance flueing is one means of compliance and ventilation is another means of compliance, sub section 8.4.2 - Where the flue terminal of a balanced flue appliance, room-sealed appliance, a fan-assisted appliance or the flue terminal of an appliance designed for outdoor installation is to be installed under a covered area, where combustion products might not readily disperse or a nuisance could occur, either—
(a) the covered area shall be open on at least two sides and the terminal shall be located to ensure a free flow of air across it is achieved; or
(b) in the case of a fan-assisted
flue appliance only, when one side is open, the terminal shall be within 500 mm of the opening, discharging in the direction of the opening and there shall be no openings into the caravan or boat along the wall within that distance and the terminal shall be located to ensure that a free flow of air across it is achieved.
The fridge and the stove/grill are both appliances design for indoor use not outdoor, outdoor appliances would be things like the Baby-Q, that's when both sides would have to be open, ventilation as a means of compliance will stop any build up of combustion products so they don't cause a nuisance, on my reading of the standard.